Existing Furnace + new mini-split

Home Support Forum Lowrise Residential Software & Compliance Existing Furnace + new mini-split

This topic contains 3 replies, has 1 voice, and was last updated by  Pat Splitt 10 months, 4 weeks ago.

  • Creator
    Topic
  • #5936

    Baba
    Participant

    If there is an existing 1 story house (no addition) and they’re using their existing furnace but also want to add a new ducted mini-split how would I model that since it’s a single zone in EP8?

Viewing 3 replies - 1 through 3 (of 3 total)
  • Author
    Replies
  • #5939

    Pat Splitt
    Participant

    There are no Energy Budget calculation requirements if all one is doing is adding AC to an existing FAU. The Code always assumes that a ducted FAU includes (at least) a minimum efficiency AC. You would be either meeting or exceeding the existing requirements for the AC efficiency. HOWEVER; check out Section 150.2 (b) 1.E. The existing duct system will have to be sealed and tested!

    Pat Splitt

    #5938

    Baba
    Participant

    Why do they want to do this? If they just want to add cooling, is there room to add an AC Condenser & Coil box to the existing furnace? Pat Splitt

    I’m not quite sure why they want to add the new system. Even if they did add an AC condenser, how can you show an existing furnace with a new AC if the system details allows you to only show one system type (existing/altered/new)?

    #5937

    Pat Splitt
    Participant

    Why do they want to do this? If they just want to add cooling, is there room to add an AC Condenser & Coil box to the existing furnace?

    Pat Splitt

Viewing 3 replies - 1 through 3 (of 3 total)